N20 energy - pheerink@gmail.com - 11-17-2026

Hello KinCony support,

I am using a KinCony N20 AC Energy Meter (order number: 4643, firmware/ESPHome version: 3.27.2) with Home Assistant. I have two problems with it, and I would like to ask for a solution or a replacement unit.

1. Correct power measurement is not possible in my 3-phase installation
My house has a 3-phase supply (L1, L2, L3). The N20 has only two voltage inputs (L1/N1 and L2/N2). At the moment I have connected one phase and bridged it to the second voltage input. The channels on the same phase as the voltage input show plausible power (W). The channels on the other phases show wrong active power. For example, my induction hob on standby (only capacitive current from its mains filter) reads about 60–70 W, with a power factor of exactly 0.87. That is what you would expect from the 120° phase shift between the CT and the voltage reference.
Even if I connect the two voltage inputs to two different phases, the circuits on the third phase still cannot be measured correctly.
Question: is there a firmware option or hardware version of the N20 (or another KinCony product) that measures all three phases correctly with 20 channels?

2. Energy (kWh) is always 0
All 20 channel energy sensors (energyX_chY.energy) and both energy_total sensors stay at 0.0, even though power and current are measured and change normally. The energy table on the device is also empty. So the device does not count energy at all.
Question: is this a known firmware issue, and how can I fix it?

I have seen in other replies on your forum that you sent a new unit to customers with similar problems. I would like to ask for the same: a replacement unit that supports my 3-phase installation and measures energy (kWh) correctly. If you need logs, screenshots or my ESPHome configuration, I am happy to send them.

Thank you in advance.

Kind regards,
Pauk Heerink


RE: N20 energy - admin - 11-17-2026

if you want use 3 phase, need use by N30 or N60, it according to hardware.