This coefficient has nothing to do with CT. It’s just a proportional relationship to the correct reading.
Posts: 3
Threads: 0
Joined: Nov 2024
Reputation:
0
Thank you. So it means the CT ratio cannot be adjusted and is fixed to 2000:1. Correct ?
How do you select the range of the CT (20 A, 100A for instance) to have a correct reading in HA ?
Posts: 9,077
Threads: 1,202
Joined: Oct 2020
Reputation:
235
Thank you. So it means the CT ratio cannot be adjusted and is fixed to 2000:1. Correct ? YES
How do you select the range of the CT (20 A, 100A for instance) to have a correct reading in HA ? Just connect different range's CT with M30, you just read data from serial port by MODBUS is ok.