N60 Loss of kWh on reset
#11
That version fixed the (obvious) bug of not showing kWh as floats. (Should really updated or delete the post I pulled 3.18 from so other people don't download old versions).
The "clear all" button did not correctly clear all the values.
Individual clear buttons did function as expected (Going to "Protocol" > "Energy" > "Energy N" and then clicking the button "Clear Energy N" did clear the kWh values for that specific bank. I tested only on bank 5 & 6.
I can't see the sourcecode to KCS to compare it to the ESPHome version of the clear buttons. Are you able to inform me what the right way to get ESPHome to have a "clear" button would be?
you can use N60 PC software, there is CLEAR button. it will send command by RS485. then you add USB-RS485 adapter, when you click button, will see what command have sent, just copy this command for your ESPHome clear button's command.
pc software download: https://www.kincony.com/forum/attachment.php?aid=9282
Thank you, I think I have an idea of what's been making this hard to figure out.
I sniffed the traffic from the App to see this for resetting chip 1's data:
01 05 02 08 ff 00 0c 40
Which decodes to running a 0x05 operation on 520 with a value of 1. I am able to replicate this exact operation with this esphome switch:
  - platform: modbus_controller
    name: "Clear Energy, Chip 1"
    register_type: coil
    address: 520
And it does what you'd expect:
[02:18:32.380][V][switch:021]: 'Clear Energy, Chip 1' Turning ON.
[02:18:32.383][V][modbus_controller.switch:090]: write_state 'Clear Energy, Chip 1': new value = ON type = 1 address = 208 offset = 0
[02:18:32.387][V][modbus:1141]: Adding frame to tx queue: 1:05:02:08:FF:00
[02:18:32.391][V][modbus_controller:534]: Command queued 5 0x208 1
[02:18:32.394][V][switch:064]: 'Clear Energy, Chip 1' >> ON
[02:18:32.415][V][modbus:807]: Write: 01:05:02:08:FF:00:0C:40 20138ms after last send, 20118ms after last receive
[02:18:32.423][V][modbus:168]: Received first byte 1 (0X1) of 8 bytes 8ms after last send
[02:18:32.426][V][modbus_controller:391]: Command ACK 0x208 2303
[02:18:32.430][V][modbus:1217]: Clearing buffer of 8 bytes - parse succeeded 16ms after last send
(Note the same sent code of "01:05:02:08:FF:00:0C:40".)
This DOES reset the kWh values.
Here's the catch, which is what has been throwing me: reset only works ONCE per power cycle. If you gain more kWh data after the reset, you can not issue the command again to re-clear the data. You must power-cycle the device before issuing the command will work. I suspect something in the ARM firmware treats this coil like a one-time invocation and then never looks for the register to change again until the whole thing re-initialized.
It'd be great if it worked multiple times in a row.
With that mystery solved, what would cause watts to be reported negative? (NONE of the ct's are on devices which generate power. All of the CT's are installed in the exact same orientation (which side faces the breaker/source). It's possible that I've flipped some red/black wires on the pos/neg inputs on the CT pins, but..for this many?
Well, I guess this works:
Additional configuration register:
- Register 30: Bidirectional CT mode (0x03 read, 0x06 write)
  - 0: Disabled
  - 1: Enabled
Turned that off... which "fixes" the problem, technically, but I feel like if I have it all wired up correctly I shouldn't be seeing negative watts.
Still want to fix it the "right" way.
you can update this new firmware for testing.
New KCS V3.27.4_beta_20261012-010554 Test Firmware:
1. Added a manual current direction reversal setting for CT sensors.
2. Extended the maximum CT sensor channel name length to 32 characters.
3. Moved “Clear All Energy Data” to the Energy → Settings page, with separate options for “Clear All Energy Data” and “Reset Calibration Factors.”
4. Added the statistics attribute to MQTT messages reported to Home Assistant.
5. Fixed missing CRC validation in certain cases that could result in incorrect data.
6. Fixed an issue on N-series energy meters where MQTT reported incorrect zero energy readings after the initial power-up.