(11-20-2021, 10:45 AM)admin Wrote: thanks for your information. the board is good. but this board have two side of relay output teminal. if install into Power Distribution Box. relay controller output wire need go to this board's right green ports. the 17-32 relay outputs' wire need covered all board go through to bottom of box. only have this problem.
we are plan to design a new extend relay module, maybe based on 8 channel, 16 channel, 32 channel.
but the most important is we will install manual button on the extend relay board. if smart controller is bad, people can use button for ON/OFF on the board, although KinCony's smart controller will not fail easily.
these are my idea, if you have some suggestions, welcome tell us. we will consider your design idea.
Thanks for the quick response.
If you're looking for suggestions, I would feel much safer to use other load terminals of a higher quality. I don't like the green connectors you currently use - they are not reliable in my opinion. Sometimes the screwing gets worn down (the screw freely spins and does not tighten well over the wire). Most of the fires in electrical boards are caused by loosened screws. For 12V DC control it is fine, but for 230V AC load it might be a real danger. I would be glad to have a product with screws of higher quality, or even without screws at all. For example this terminals block uses screwless push-in wire which is much safer: https://www.wago.com/global/pcb-terminal.../p/253-112