KC868-A8 PCB V1.7 - Maximum continuous DC load ratings
I would like to confirm the maximum continuous load current ratings of the KC868-A8 PCB V1.7 when switching 12V DC resistive heating loads.
1. What is the maximum permissible continuous current per relay output, considering the complete output circuit (relay contacts, PCB traces, solder joints and terminal blocks), rather than just the relay's nominal contact rating?
2. Can multiple relay outputs, up to all eight, carry their maximum rated current simultaneously for extended periods, or are there any combined load limits or current derating requirements?
If available, could you please provide the corresponding current limits in amperes (A) for PCB V1.7?
Thank you!
Dami
1. terminal max 10A. pcb tracking max 10A is ok. You can also apply a thicker layer of tin to the PCB traces on the reverse side.
2. Each channel is independent and unrestricted.