KinCony N30 – CT clamp selection for 100–225 A three-phase circuits (university solar
#1
Subject: KinCony N30 – CT clamp selection for 100–225 A three-phase circuits (university solar monitoring project)

Hello KinCony team,

We are a computer engineering student team planning to use the KinCony N30 to monitor a campus solar PV installation. The circuits are three-phase, 4-wire (3P4W), nominal 240 V (we are still confirming whether this is line-to-line or line-to-neutral), with breakers rated 125 A and 225 A and expected design currents of about 96 A and 180 A. We would like to confirm the following before ordering.

1. CT clamp model: Please share the specification of the OPCT24ATL clamp listed on your website: rated primary current, turns ratio, and output type (current in mA or voltage in mV). Is it compatible with the N30 at up to 250 A?

2. Maximum current: The N20 product page states "support use by MAX 250A CT clamp sensor" and also lists a "2000:1 CT clamp voltage sensor". Is the same 250 A limit valid for the N30? Which exact CT part and ratio do you recommend for 160 A and 225 A circuits?

3. Burden resistors and input limit: We understand that each CT input has two 5.1 Ω burden resistors (10.2 Ω in total) and that the CT output must stay below 700 mV differential. With these values, a 2000:1 CT would give about 1.15 V at 225 A. Is our understanding correct? Is the 700 mV limit a peak or an RMS value, and what happens if it is exceeded?

4. Voltage-output CTs: If we use a CT with voltage output (for example 1 V at rated current), must the on-board burden resistors be removed or bypassed, and how is accuracy affected?

5. Accuracy: What accuracy (energy class or percentage) do you specify for the N30 with the recommended CT, and over what current range?

6. Phase assignment: We understand that CT channels 1–10 belong to phase A, 11–20 to phase B and 21–30 to phase C, because each BL0910 chip is tied to one voltage input. Is this correct? Can four three-phase feeders be monitored with 12 CTs on one N30 sharing one set of voltage connections?

7. RS485: Can the N30 RS485 port act as a Modbus master, or is it slave only?

8. Logging and outages: Can SD card logging be set faster than hourly? During a Wi-Fi or MQTT outage, does the N30 store the missed measurements and send them afterwards, or does it only keep the accumulated energy totals?

9. Price and shipping: What is the N30 price, are CT clamps included, and do you ship to the Philippines?

Thank you for your help. Any datasheet or wiring guidance would be appreciated.

Best regards
Reply
#2
1. N series energy meter board support CT sensor are:
https://shop.kincony.com/products/ct-cla...9e2e&_ss=e
they are "CURRENT" type.

2. YES, N10,N20,N30,N60 use by same CT sensor.

3. https://www.kincony.com/forum/showthread.php?tid=8612

4. not need remove if use "voltage" CT sensor, just "current" type is better. "voltage" also can use.

5. support 0.001kwh.

6. YES, this video have explained in details: https://youtu.be/P8Rbdpg2EhQ

7. N30 RS485 connect with ARM CPU, work as "SLAVE".

8. when wifi or network disconnected, also can save to SD card. it work in local ESP32 chip. Can't set the interval time for SD card.

9. just order from online shop directly, in stock. CT sensor not included in N30.