I have a 24v 4-20ma Pressure transmitter connected to A3 but the raw measurements even with zero pressure fluctuate.
What is the best way of connecting this for maximum accuracy and stable numbers.
In ESPHome, this is mu code and the Zero Pressure fluctuates by 100
(08-14-2025, 05:14 AM)admin Wrote: Do you have another analog sensor? or you can test with a static voltage, such as 3.3v. see the value whether stable showed in webpage.
Unfortunately I do not. Theyre all pulsed outputs.
Can I hook up a potentiometer to it? 150 ohm across 3.3v and gnd and the wiper into A3 and then check the stability mid range?
08-19-2025, 04:34 AM (This post was last modified: 08-19-2025, 04:37 AM by Onepointbrewing.)
Im having trouble with a pressure transmitter (4-20mA @24v).
It suffers from decay over a period of time. I asked chatGPT to help out and it says that its caused by “the repeated conversions act like a little pump that drags the node down, so the reported value “decays” over minutes/hours” Ok so I get it (sort of) so I installed a 250ohm shunt resistor between the ADC IP (the op of the sensor) and GND. It also suggests installing a 0.1uF cap in the same spot (in parallel w the shunt resistor) 1: this stabilizes the measurement for approx 2-3hrs and then the decay resumes. Would a lower resistsor give me a more reliable time duration??? 2: Not sure about the 0.1uF cap except for reducing line noise… Is this correct and can someone point me to a picture somewhere in the internet that shows a cct diagram. Thanks
i have isolated the code and its not to do with the code, its the electronics side.
So is the cct below a better way of fixing the issue????