kc868-a6 analog input
#1
How do you connect a thermistor to an analog input?
Reply
#2
if your signal is 0-5v or 4-20mA, it's ok.
Reply
#3
(09-21-2026, 11:38 PM)admin Wrote: if your signal is 0-5v or 4-20mA, it's ok.

For a thermistor, would you recommend using a voltage divider with a fixed resistor, and is there a specific resistance value or wiring diagram you suggest for the KC868-A6? Also, does the analog input need any calibration to convert the voltage reading into temperature?
Reply
#4
if use thermistor, suggest chose A24 or CO16 controller, that support PT100 sensor directly.
Reply